Communication / MQTT
MiniHPC is capable of sending measured data and adjusting its settings via the MQTT protocol.
To enable this feature, it is first necessary to configure MiniHPC's access to the local MQTT broker. After opening the device's IP address, select the MQTT menu. You will be prompted to enter the username and password, which are provided in the 9.2 WiFi AP menu.
: turns MiniHPC's access to the configured MQTT broker on or off.
: the IP address of the MQTT broker on the local network.
: the TCP port of the MQTT broker.
: the username for accessing the MQTT broker.
: the password for accessing the MQTT broker.
: an optional name for the initial topic on which MiniHPC will send measured data and listen for configuration changes. If there are multiple MiniHPC devices on the MQTT network, it is necessary to choose a unique root topic for each device.
: the topic on which MiniHPC listens and, once any content is detected, sends the entire configuration and all measured data to the MQTT server (typically upon a Home Assistant restart).
: determines the time intervals at which MiniHPC sends measured data to the MQTT server.
In case of a successful connection of MiniHPC to the MQTT server, the status Connected will be displayed in the section of the 9.1 WiFi station menu.
MQTT settings
For viewing all available data, we recommend the MQTT explorer application.
MQTT explorer
MiniHPC uses 6 topics for displaying data and setting parameters:
- displays the measured data. The data is updated only when a change occurs for the given item. All measured data will be displayed upon MiniHPC startup or whenever any setting is changed in MiniHPC.
- displays the current MiniHPC configuration.
- topic for sending configuration changes.
- topic for sending a configuration change that will be applied but not saved to MiniHPC's memory. MiniHPC's memory has a limited number of write cycles, and under normal use, it does not get damaged. However, if an automated script is used to modify parameters multiple times per minute, it is recommended to use this topic.
- topic for sending external sensor values.
- topic for sending control commands.
For the set and setsensor topics, you can send a single value or a set of values in JSON format.
Changes in the topics set, setns, setsensor, and cmd will only be allowed if permissions are enabled in menu 9.4 Permissions
Description of the Data Output from the MQTT Topic miniHPC/data/# or the file data.json
Name Multiplier Description
t1 1°C Temperature T1
t2 1°C Temperature T2
t3 1°C Temperature T3
t4 1°C Temperature T4
t5 1°C Temperature T5
t6 1°C Temperature T6
tout 1°C External temperature
tsuc 1°C Temperature at the evaporator
texh 1°C Temperature at the compressor discharge
outMode -- Outdoor unit mode: Cool-, Dry-, Fan-, Heat-
outState -- Compressor state: 0 - off; 1 - on
outFrequency 1Hz Compressor frequency
outFan 1RPM Speed of the outdoor unit's fan
outPower 1W Compressor power consumption
outEEV -- Position of the expansion valve
outEEV2 -- Position of the 2nd expansion valve (if is available)
outDCbus 1V Voltage at the inverter output
outDefrost 1/0 Defrost status
outDCcurrent 1A Current drawn by the compressor
flow 1l/min Flow of the heating water
tset 1°C Set temperature by the regulator
tIDUroom 1°C Tpreset from the 4.1 Outdoor unit menu
tIDUset 1°C Tamb from the 4.1 Outdoor unit menu
R1 1/0 Relay R1 status
R2 1/0 Relay R2 status
R3 1/0 Relay R3 status
R4 1/0 Relay R4 status
R5 1/0 Relay R5 status
S1 1/0 Input S1 status
S2 1/0 Input S2 status
pwrOutHP 1W Current output energy of the heat pump
heatTimeHP 1s Compressor runtime during heating
heatTimeELH 1s Runtime of the electric auxiliary heater on R2
heatTimeDefr 1s Total defrosting time
heatCountHP 1x Number of compressor starts during heating
heatCountELH 1x Number of electric heater activations on R2
heatCountDefrost 1x Number of defrost cycles
coolTimeHP 1s Compressor runtime during cooling
coolCountHP 1x Number of compressor starts during cooling
dhwLegTime 1s Time of the last anti-legionella heating (since 1.1.1970)
dhwTimeHP 1s Compressor runtime during TPV heating
dhwTimeELH 1s Electric TPV heating runtime via relay R1
dhwCountHP 1x Number of compressor starts during TPV heating
dhwCountELH 1x Number of relay R1 activations for electric TPV heating
heatPwrIn 1mWh Electrical energy consumed for heating
coolPwrIn 1mWh Electrical energy consumed for cooling
dhwPwrIn 1mWh Electrical energy consumed for TPV heating
heatPwrOutHP 1mWh Thermal energy produced for heating
heatPwrOutELH 1mWh Thermal energy produced by electric auxiliary heating for heating
coolPwrOut 1mWh Thermal energy removed by cooling
dhwPwrOut 1mWh Thermal energy produced for TPV heating
pwrDefrIn 1mWh Energy consumed during defrosting
pwrDefrOut 1mWh Energy removed during defrosting
comprTime 1s Total compressor running time
comprCount 1x Total number of compressor starts
BTtemp 1°C BT sensor temperature
BThum 1% BT sensor relative humidity
BTbat_mv 1mV BT sensor battery voltage
BTbat_lev 1% BT sensor battery level
BTrssi 1dBm BT sensor signal strength
Description of the Configuration from the MQTT Topic miniHPC/config/# or the file config.json
Setting (key) Default Min Max Multiplier Description
mode 0 0 2 -- Mode: 0 - off; 1 - Heating; 2 - Cooling
heating_onoff_input 0 0 5 -- 1.1 Enable heating based on: 0 - Always on; 1 - Thermostat S2; 2 - Flow meter S1/I1; 3 - T1 as thermostat; 4 - S2 + S1/T1; 5 - S2 + T1; 6 - S1/I1 + T1
heating_reg_input 1 0 2 -- 1.2 Temperature regulation based on: 0 - T1 room temperature; 1 - T2/T3 fixed output; 2 - T2/T3 output/equithermal
heating_t1_hysteresis 5 1 50 0.1°C 1.1 T1 as thermostat - hysteresis
heating_reg_temp 2 2 3 -- 1.2 Temperature regulation: 2 - T2; 3 - T3
temperature_T1 250 100 300 0.1°C 1.2 / 2.2 T1 - room temperature
temperature_T3 35 15 55 1°C 1.2 T2/T3 - output water/fixed - heating
temperature_T3_cool 20 10 25 1°C 2.2 T2/T3 - output water/fixed - cooling
heating_eqtr_m10 40 20 50 1°C 1.3 T2/T3 temperature at -10°C outside
heating_eqtr_p10 25 20 50 1°C 1.3 T2/T3 temperature at +10°C outside
heating_eqtr_offset 0 -9 9 1°C 1.3 Custom equithermal offset
heating_eqtr_avg 24 0 24 1h 1.3 Averaging of the external temperature
heating_eqtr_t1off 0 0 100 0.1x°C 1.3 T2/T3 offset based on T1
heating_schedule_time 360,720,1020,1320 0 1439 1 min 1.4 Timer - times
heating_schedule_offset 0,0,0,0 -100 100 0.1°C 1.4 Timer - offsets
heating_schedule_affect 7 0 7 -- 1.4 Timer - affects
Bit mask: 1 - T1, 2 - T2/T3, 4 - Eqtr
heating_elh_mode 0 0 3 -- 1.5 Electric heating R2 - mode: 0 - HP; 1 - HP+EH; 2 - HP/EH; 3 - EH
heating_elh_out_temp -5 -20 20 1°C 1.5 Electric heating outdoor temperature
heating_elh_delay 120 10 600 1min 1.5 Delay for electric heating activation
heating_elh_offset 20 1 50 0.1°C 1.5 Electric heating - hysteresis
heating_pump_delay 60 5 3600 1sec 1.6 R3 pump - delay time for turning off heating
heating_pump_ps 0 0 1 -- 1.6 Power save: 0 - off; 1 - on
cooling_onoff_input 0 0 3 -- 2.1 Enable cooling based on: 0 - Always on; 2 - S2inv; 3 - T1; 4 -S1/I1; 5 - S2 + T1; 6 - S2 + S1/I1; 7 - S2inv + T1; 8 - S2inv + S1/I1; 9 - T1 + S1/I1
cooling_reg_input 0 0 1 -- 2.2 Cooling regulation based on: 0 - T1 room temperature; 1 - T3 output water/fixed
cooling_t1_hysteresis 5 1 50 0.1°C 2.1 T1 as thermostat - hysteresis
cooling_schedule_time 360,720,1020,1320 0 1439 1 min 2.3 Timer - times
cooling_schedule_offset 0,0,0,0 -100 100 0.1°C 2.3 Timer - offsets
cooling_schedule_affect 3 0 3 -- 2.3 Timer - affects
Bit mask: 1 - T1, 2 - T3
cooling_pump_delay 60 5 3600 1sec 2.4 R3 pump - delay time for turning off cooling
cooling_pump_ps 0 0 1 -- 2.4 Power save: 0 - off; 1 - on
cooling_3wayV 1 0 1 -- 2.5 3-way valve R5 for cooling: 0 - Off; 1 - On
cooling_3wv_inv 0 0 1 -- 2.5 Inverted output for 3-wv on R5 relay: 0 - Off; 1 - On
cooling_bt_enable 0 0 1 -- 2.6 Read BT sensor: 0 - Off; 1 - On
cooling_dp_offset 0 -100 100 0.1°C 2.6 Dew point offset for cooling
ntc_t1_by_bt 0 0 1 -- 2.6 Replace T1 NTC temperature with BT temperature: 0 - Off; 1 - On
dhw_onoff 0 0 1 -- 3.1 Domestic Hot Water (DHW) heating: 0 - Off; 1 - On
dhw_temp_diff 20 5 50 1°C 3.1 Switching differential
dhw_temp_target 55 20 80 1°C 3.1 Target DHW temperature
dhw_schedule_time 360,720,1020,1320 0 1439 1 min 3.2 Timer - times
dhw_schedule_offset 0,0,0,0 -20 20 1°C 3.2 Timer - offsets
dhw_schedule_affect 1 0 3 -- 3.2 Timer - affects
1 - Target temperature; 2 - Switching differential; 3 - both
dhw_al_frequency 7 1 30 1 day 3.3 Anti-legionella - frequency
dhw_al_day 6 1 7 -- 3.3 Day of the week
1 - Monday; 2 - Tuesday; 3 - Wednesday; 4 - Thursday; 5 - Friday; 6 - Saturday; 7 - Sunday
dhw_al_time 120 0 1439 1 min 3.3 Time - minute
dhw_al_temp 65 10 80 1°C 3.3 Target temperature
dhw_temp_hp 45 0 55 1°C 3.4 Max DHW temperature T5 for HP
dhw_hp_time 90 30 240 1min 3.4 Max HP runtime
dhw_temp_t6 56 20 60 1°C 3.4 Max T6 temperature
dhw_out_min -20 -35 +20 1°C 3.4 Min. outdoor temperature
dhw_out_max 50 20 50 1°C 3.4 Max. outdoor temperature
dhw_pump_delay 60 5 3600 1sec 3.5 R3 pump - delay time for turning off DHW
dhw_elh_mode 0 0 2 -- 3.6 Electric heating - mode: 0 - only R1; 1 - turn on R1+R3+R4; 2 - turn on R2+R3+R4
dhw_3wv_defroff 0 0 1 -- 3.7 Disable 3-way valve R4 during defrost: 0 - Off; 1 - On
dhw_3wv_inv 0 0 1 -- 3.7 Inverted output for 3-wv on R4 relay: 0 - Off; 1 - On
flow_imp 476 1 1000 1imp/l 7.3 Flow meter calibration
power_input 0 0 2 -- 7.4 Input electrical energy: 0 - Outdoor unit; 1 - External meter on S1; 2 - External meter on S2
odu_power_calib 0 -100 100 0.5% 7.4 Outdoor unit power calibration
power_input_pulses 10 1 100 100pulses/kWh 7.4 External meter calibration for S1/S2
power_limit 0 0 5000 W 7.4 Power limit
cal_idu_heat_pid 0 0 1 -- 7.5 Ragulation 0-IDU sim; 1-PID
cal_idu_heat_pidMinF 30 15 85 1 7.5 Min frequency
cal_idu_heat_pidMaxF 85 30 120 1 7.5 Max frequency
cal_idu_heat_pidP 50 0 255 1 7.5 P
cal_idu_heat_pidI 12 0 255 1 7.5 I
cal_idu_heat_pidD 10 0 255 1 7.5 D
cal_idu_heat_preset 22 16 30 1°C 7.5 Preset temperature
cal_idu_heat_offset 6 2 10 0.5°C 7.5 Temperature offset
cal_idu_heat_uplimit 6 1 10 0.5°C 7.5 Upper limit
cal_idu_heat_downlimit 10 2 20 0.5°C 7.5 Lower limit
cal_idu_heat_gain 10 1 30 0.1 7.5 Temperature gain
cal_idu_cool_pid 0 0 1 -- 7.6 Regulation 0-IDU sim; 1-PID
cal_idu_cool_pidMinF 30 15 85 1 7.6 Min frekvency
cal_idu_cool_pidMaxF 85 30 120 1 7.6 Max frekvency
cal_idu_cool_pidP 15 0 255 1 7.6 P
cal_idu_cool_pidI 30 0 255 1 7.6 I
cal_idu_cool_pidD 0 0 255 1 7.6 D
cal_idu_cool_preset 22 16 30 1°C 7.6 Preset temperature
cal_idu_cool_offset 0 -4 2 0.5°C 7.6 Temperature offset
cal_idu_cool_downlimit 10 2 10 0.5°C 7.6 Lower limit
cal_idu_cool_gain 10 1 30 0.1 7.6 Temperature gain
cal_idu_dhw_preset 30 20 30 1°C 7.7 Preset temperature
cal_idu_dhw_offset -10 -20 10 0.5°C 7.7 Temperature offset
cal_idu_dhw_ff 0 30 120 1 7.7 Fixed frequency 0-IDU sim; >30-FF
comp_fr_hight 40 30 50 1Hz 7.8 Maximal frequency at selected temperature (+25°C)
comp_fr_lowt 90 40 120 1Hz 7.8 Maximal frequency at temperature 0°C for CH
comp_fr_lowt 90 40 120 1Hz 7.8 Maximal frequency at temperature 0°C for DHW
comp_fr_temp 25 10 30 1°C 7.8 Outdoor temperature
protect_fs 2 0 3 -- 8.1 Flow protection
Bit mask: 1 - Flow switch S1, 2 - Flow sensor I1
protect_fselm 50 20 250 0.1l/min 8.1 Flow sensor I1 limit
protect_fs_time 60 1 240 1sec 8.1 Time without protection at startup
protect_fs_err 1 1 100 0.1sec 8.1 No flow error after
protect_defr_t3 100 50 250 0.1°C 8.2 Minimum temperature T3
protect_anfreeze_t6 50 20 250 0.1°C 8.2 Activate R3 pump below T6 temperature
protect_t6_temp -5 -20 5 1°C 8.2 Temperature for T6 error
protect_t6_time 30 1 240 1sec 8.2 Time for T6 error
protect_anblock_r3t 10 0 60 1sec 8.3 Protection against R3 blockage - time
protect_anblock_r3d 3 1 30 1days 8.3 Protection against R3 blockage - delay
protect_anblock_r4t 60 0 60 1sec 8.3 Protection against R4 blockage - time
protect_anblock_r4d 3 1 30 1days 8.3 Protection against R4 blockage - delay
protect_anblock_r5t 60 0 60 1sec 8.3 Protection against R5 blockage - time
protect_anblock_r5d 3 1 30 1days 8.3 Protection against R5 blockage - delay
protect_overload 0 0 1 -- 8.4 Do not turn on R1 and R2 simultaneously: 0 - Off; 1 - On
odu_heat_relay 0 0 5 -- 8.5 Relay switching DHW heating: 0 - Off; 1 - R1; 2 - R2; 4 - R4; 5 - R5
odu_heat_outt 0 -15 5 1°C 8.5 Outdoor temperature threshold
odu_heat_time 5 1 60 1min 8.5 Heating time
odu_heat_adds 30 0 240 1s/1°C 8.5 Additional time
time_tz_sync 0 0 1 -- 12.1 Auto-sync by web: 0 - Off; 1 - On
odu_power_limit 0 0 2 -- 13.2 Outdoor unit power limit: 0 - No limit; 1 - Level 1 (70%); 2 - Level 2 (50%)
odu_power_limit_time 0 0 1 -- 13.2 Time-based activation: 0 - Off; 1 - On
odu_power_limit_from 1320 0 1439 1 min 13.2 Start
odu_power_limit_to 360 0 1439 1 min 13.2 End
odu_night_mode 0 0 2 -- 13.3 Night mode: 0 - Off; 1 - Always on; 2 - Time-based
odu_night_mode_from 1320 0 1439 1 min 13.3 Start
odu_night_mode_to 360 0 1439 1 min 13.3 End
odu_quiet 0 0 1 -- 13.4 Quiet mode: 0-Off; 1-On
odu_quiet_frlow 30 30 50 1 Hz 13.4 Low RPM frequency
odu_quiet_frhigh 50 50 70 1 Hz 13.4 high RPM frequency
odu_quiet_temp 5 -10 20 1 °C 13.4 Outdoor temperature
odu_quiet_add 20 0 50 10 RPM 13.4 Speed add
odu_quiet_rpmlow 45 10 70 10 RPM 13.4 Minimal speed
odu_defrCtrl 1 0 1 -- 13.5 Defrost control: 0-Off; 1-On
odu_defrFr 50 30 80 1 Hz 13.5 Minimal frequency
odu_defrTE 10 5 20 1 °C 13.5 End temperature
odu_defrEEV 300 150 400 --- 13.5 EEV value
odu_defrTrig 1 0 1 -- 13.6 Defrost trigger: 0-Off; 1-On
odu_defrTr_mint 30 15 50 1 min 13.6 Minimal time
odu_defrTr_maxt 240 60 480 1 min 13.6 Maximal time
odu_defrTr_delta 10 5 15 1 °C 13.6 Delta T
odu_defrTr_temp -10 -20 0 1 °C 13.6 outdoor temperature
eev_ctrl 0 0 3 -- 13.7 EEV control: Bit mask: 1 - heating, 2 - cooling
eev_ctrl_cal 100 80 120 1 % 13.7 Calibration
eev_ctrl_min 70 50 100 --- 13.7 Minimal EEV value
eev_ctrl_start 300 100 360 --- 13.7 Start EEV value
bt_amm_temp 0 0 2 -- Calculation of BT temperature: 0 - averaging; 1 - minimal; 2 - maximal
bt_amm_hum 2 0 2 -- Calculation of BT humidity: 0 - averaging; 1 - minimal; 2 - maximal
bt_act_new 1 0 1 -- Activation of new BT sensors: 0 - disabled; 1 - enabled
bt_cloud 5 0 60 1 min Upload interval of BT data to the cloud
Method for Modifying the Configuration via the MQTT Topic miniHPC/set
Individual configuration parameters of MiniHPC can be modified via the MQTT topic miniHPC/set/PARAMETER. Instead of the value PARAMETER, you substitute the specific variable name from the table above.
For example, to send a new value for the output water temperature T3 (variable temperature_T3) to 33°C, send the value 33 to the MQTT topic miniHPC/set/temperature_T3.
If you need to modify several variables at once, you can use the JSON string method and send them to the topic: miniHPC/set/json. For example, to modify the variables dhw_temp_target and dhw_temp_diff in one step, construct the JSON string:
{"dhw_temp_target": 60, "dhw_temp_diff": 10}
For automated scripts that regularly adjust the configuration, please use the MQTT topic miniHPC/setns/PARAMETER, which applies the change but does not permanently save it to MiniHPC's memory.
Method for Sending Values from External Sensors via MQTT
MiniHPC has the ability to receive values from some sensors via MQTT and thereby replace their physical connection to MQTT. The sent value will be retained in memory for 60 minutes and then will expire. Therefore, it is necessary to send these values regularly at intervals shorter than 1 hour. Ideally, for example, once per minute.
Sensor Unit Description
T1 1.00°C Replacement of the indoor temperature T1
Tout 1.00°C Replacement of the external temperature measured by the outdoor unit of the air conditioner
RH 1.00% Indoor relative humidity
Individual values of external sensors can be sent via the MQTT topic miniHPC/setsensor/SENSOR. Instead of the value SENSOR, you substitute the specific sensor name from the table above.
For example, to send the room temperature T1 value of 24.56°C, send the value 24.56 to the MQTT topic miniHPC/setsensor/T1.
If you need to modify several sensors at once, you can use the JSON string method and send them to the topic: miniHPC/setsensor/json. For example, to send sensors T1 and RH in one step, construct the JSON string:
{"T1": 24.56, "RH": 45.56}
Sending Control Commands via MQTT
Some MiniHPC functions, such as starting DHW heating or defrosting the outdoor unit, can be controlled by commands sent via MQTT.
COMMAND VALUE Description
dhwonStart DHW heating
dhwoffStop ongoing heating
dhwalForce DHW heating to the temperature set in menu 3.3 Anti-legionella
dhwturboEnable turbo DHW heating (compressor heating simultaneously with electric DHW heating)
odudefrostManually start defrosting of the outdoor unit
resetdevMiniHPC software restart
reseterrorClear error message
Each command with its value can be sent via the MQTT topic miniHPC/cmd/COMMAND. Replace COMMAND with the specific command from the table above, and the value will be used as the MQTT payload.
For example, to start DHW heating, send the value on to the MQTT topic miniHPC/cmd/dhw.