Calibration Menu / 7.5 - IDU Heating Temperatures
The second method, labeled as , allows MiniHPC to directly send requests to the outdoor unit to set the exact compressor frequency, using the PID controller built into MiniHPC for the calculation. This regulation method is, in most cases, more precise than IDU sim, preventing unwanted oscillations and compressor cycling.
IDU sim
To be able to configure this part of the menu, it is first necessary to understand how the air conditioner regulates its output based on the set temperature (Tpreset) and the room temperature (Tamb).
MiniHPC operates by simulating a connected standard indoor unit. It sends the outdoor unit data about the set temperature and the measured room temperature (in addition to other parameters such as the liquid refrigerant temperature, mode, fan speed, silent mode, etc.).
The outdoor unit then decides, based on these parameters, whether to turn the heating on or off and, if it is already on, whether to reduce or increase the output.
The only parameter that MiniHPC manipulates is the room temperature (Tamb), by sending the outdoor unit a Tamb value calculated using the formula:
If the difference between the actually measured temperature and the set temperature is greater than this limit, the outdoor unit will receive the value of this limit. (After exceeding this limit by 3.5°C, this function is disabled and the outdoor unit receives the real values as a prevention against overheating. At that moment, the outdoor unit turns off the heating.)
Temperatures higher than 2°C in this setting do not make sense because if the temperature exceeds the limit by more than 2°C, the outdoor unit will turn off the heating anyway. By default, this limit is set to 3°C, meaning that the behavior is as if this limit were not applied, since the outdoor unit turns off the heating before the limit would come into effect.
The setting is useful when the outdoor unit begins to cycle during the compressor startup. In reality, especially during transitional seasons, when the compressor is turned on, it typically runs at about 50% capacity and then, after a few minutes, modulates its output either up or down. However, in some cases, that 50% may be too much, causing the heating water temperature to rise quickly, which results in the temperature threshold being exceeded and the compressor turning off. After the temperature drops for a few minutes, it turns on again, and so on.
Thanks to this function, if the switching temperature is exceeded, a slightly lower temperature is sent to the outdoor unit so that it believes it has not exceeded the threshold. At the same time, that temperature will be high enough to force the outdoor unit to modulate its output lower, thus regulating the output within the proper range without cycling.
PID
When selecting the PID controller option, it is possible to limit the compressor frequency range, set the upper temperature limit, and adjust individual PID controller components.
This situation may occur when the heating water reaches the set temperature, the PID controller gradually reduces the compressor frequency to the Minimum Frequency limit, and if the heating output at this frequency still exceeds the required heat to maintain the set temperature, the output heat exchanger temperature will continue to rise until it reaches the Up Temperature Limit.
For control based on outlet water temperature T3, the default preset values are: P:15, I:30, D:0
These values should be adjusted according to the actual behavior of the PID controller in the specific heating system.
After reaching a temperature T6 higher than 55°C, the PID controller automatically starts to reduce the compressor frequency to maintain this temperature at 55°C.
When the compressor discharge temperature reaches 95°C or higher, the PID controller will automatically reduce the compressor frequency to prevent the discharge temperature from rising further.